You are here: Home   →   Documents   →   Information Sheets   →   High R-Value Wall Assemblies   →   High R-Value Wall Assembly-09: Flash-and-Fill Hybrid Wall Construction
ETW
Enclosures That Work
By Building Science Corporation   Created: 2009/06/04
  • 2x6 wood frame wall at 24" o.c.
  • 2" high density spray foam
  • Fiberglass or cellulose cavity insulation
  • OSB sheathing
  • Housewrap
Scoring: How It Rates
Thermal Control4
Durability4
Buildability4
Cost3
Material Use4
Total
19
The hybrid wall system significantly reduces air leakage over standard construction or advanced framing, which conserves energy, and reduces the potential for both air leakage and vapor condensation durability issues. Unfortunately, the added cost of the spray foam insulation only adds a minimal amount to the R-value since the thermal bridging of the wall is not addressed. Addressing the thermal bridges would improve this wall construction.
This Information Sheet summarizes flash-and-fill hybrid wall construction including the advantages and disadvantages of this construction strategy. A more detailed analysis and direct comparison to several other walls can be found online.1 The scoring system is subjective based on the relative performance and specifications between different wall systems. Complex two dimensional heat flow analysis and one dimensional hygrothermal modeling were used to determine moisture related durability risks for analysis.
Installed insulation R-value: The installed R-value is approximately R-12 for two inches of high density spray foam (2.0 pcf) and R-13 for three and a half inches of fiberglass batt, totaling R-25.
Whole-wall R-value: Using two dimensional heat flow analysis with thermal bridging effects and average framing factors, the R-value decreases from an installed insulation R-value of R-25 to whole wall R-value of approximately R-17 for a the hybrid wall construction in this case.1 The decrease in R-value is due to the thermal bridging of the wall framing, top and bottom plates.
Air Leakage Control: Fiberglass batt, and both blown and sprayed cellulose are air permeable materials allowing possible air paths between the interior and exterior as well as convective looping in the insulation. Although densepack cellulose has less air permeance it does not control air leakage. In the case of the hybrid wall system, the spray foam is used as an air barrier in the stud space to limit the air movement between the interior and exterior so there are fewer energy losses due to air leakage. It is still possible and common to get air leakage below the bottom plate if is not sealed.2 When spray foam is used in the wall system, it is beneficial to also use it in the rim joist which has a high potential for air leakage.
Typical Insulation Products: Spray foam insulation and fiberglass batt, blown fiberglass, blown cellulose, or sprayed cellulose.
Durability
Rain Control: Rain leakage into the enclosure is the leading cause of premature building enclosure failure. Rain control is typically addressed using a shingle lapped and/or taped drainage plane such as building paper or a synthetic WRB (i.e. homewrap). Intersections, windows, doors and other penetrations must be drained and/or detailed to prevent the penetration of rainwater beyond the drainage plane.3
Air Leakage Control: Air leakage condensation is the second largest cause of premature building enclosure failure with wood framed wall construction. It is very important to control air leakage to minimize air leakage condensation durability issues. An air barrier is required in this wall system to ensure that through-wall air leakage is eliminated (ideally) or at least minimized. An air barrier should be stiff and strong enough to resist wind forces, continuous, durable, and air impermeable.4
In the hybrid wall system, two inches of spray foam is used as an air barrier to reduce the air leakage. This also reduces the air leakage condensation against the sheathing in the winter as it significantly warms the condensation plane. Since air leakage from the interior, into the studspace and back into the interior can also cause condensation in some climates, it is still important to detail the interior surface as an air barrier as well.
Vapor Control: Fiberglass and cellulose are vapor permeable materials, but including two inches of high density spray foam acts as a vapor barrier limiting vapor movement to the cold exterior sheathing, and significantly reduces the risk of vapor condensation durability issues. High density spray foam also decreases the summer inward vapor drives. If low density spray foam is used, it is not a vapor barrier, and other vapor control may be required depending on the climate. Calculations should be done to ensure a minimum risk to vapor condensation durability issues.5
Drying: Using high density spray foam will slow the movement of moisture across the enclosure. and there is no moisture buffering capacity or redistribution within the spray foam. Some vapor control may still be required at the interior surface in cold climates which slows drying. Proper flashing of all penetrations should help minimize moisture in the enclosure. Ventilation behind vapor impermeable claddings and interior components (e.g. kitchen cabinets) can encourage drying.
Built-in Moisture: Care should always be taken to build with dry materials where possible, and allow drying of wet materials before close in. High density spray foam may slow drying across the enclosure since it is a vapor barrier. In geographic regions with reduced drying potential, the moisture content of the sheathing may stay elevated for an extended period due to the inability to dry or redistribute moisture into the wall. Ventilated claddings are recommended.
Durability Summary: Hybrid wall construction has a greater resistance to both air leakage condensation and vapor diffusion condensation because of the high density spray foam increasing the dew point of the condensation surface. The primary durability risks associated with these wall assemblies involve moisture damage related to rain water penetration.
Buildability
Hybrid wall construction is not very different from standard wall construction or advanced framing. By filling the stud space with two inches of spray foam, an R-13 batt can still easily be installed against the foam, or cellulose could be sprayed in the remaining stud space. All other aspects of the construction are the same as standard construction or advanced framing. Using high density spray foam reduces the risks from poor workmanship during construction.
Cost
Using spray foam insulation can be costly, and while it reduces the risks of moisture related durability issues, the minimal increase in R-value due to the thermal bridging may not be worth the increased cost of the spray foam insulation.
Material Use
There is no increase in framing materials from standard construction, but the embodied energy of the system increases with the addition of high density spray foam insulation.
Total Score
The hybrid wall system significantly reduces air leakage over standard construction, which conserves energy, and reduces the potential for both air leakage and vapor condensation durability issues. Reducing the air leakage may also increase occupancy comfort by reducing drafts. Unfortunately, the added cost of the spray foam insulation only adds a minimal amount to the R-value since the thermal bridging of the wall is not addressed. This wall is very similar to build as standard construction and less susceptible to poor workmanship during construction. Addressing the thermal bridges would improve this wall construction.
  2. Straube, J. (2009, 04 22). BSD-014 Air Flow Control in Buildings. Retrieved from buildingscience.com.
  4. Lstiburek, J. (2008, 08 20). BSD-104: Understanding Air Barriers. Retrieved from buildingscience.com.