You are here: Home   →   Documents   →   Information Sheets   →   High R-Value Wall Assemblies   →   High R-Value Wall Assembly-06: SIPs Wall Construction
ETW
Enclosures That Work
Created: 2009/06/04
  • OSB interior and exterior panels
  • EPS insulation core typical
  • Housewrap
Scoring: How It Rates
Thermal Control4
Durability4
Buildability3
Cost3
Material Use3
Total
17
The typical SIPs panels are not constructed with enough insulation to be considered high-R assemblies in heating climates. SIPs installation requires specialized training but is quicker and easier than wood framed construction following training. Historical moisture related durability issues with SIPs have been solved with a better understanding of building science, and air tightness details.
This Information Sheet summarizes SIPs wall construction including the advantages and disadvantages of this construction strategy. A more detailed analysis and direct comparison to several other walls can be found online.1 The scoring system is subjective based on the relative performance and specifications between different wall systems. Complex two dimensional heat flow analysis and one dimensional hygrothermal modeling were used to determine moisture related durability risks for analysis.
Installed insulation R-value: Structural Insulated Panels (SIPs) are typically constructed using OSB panels adhered to both sides of an expanded polystyrene (EPS) foam insulation core. The most common SIP insulation thicknesses are 3.5” and 5.5” and are equivalent to R-14 and R-22. It is possible, although not as common, to use different insulation types, and thicker panels to achieve high R wall values.
Whole-wall R-value: Using two dimensional heat flow analysis with thermal bridging effects and average framing factors, the clear wall R-value with the OSB layers, drywall, cladding, and surface films often has an R-value higher than the installed insulation R-value because of fewer thermal bridges in the wall system. The whole-wall R-value depends on thermal bridging through vertical stiffeners, top and bottom plate, as well as the wood bucks for windows and doors.1
Air Leakage: Both OSB and EPS foam are air impermeable so there is no air leakage through the centre of the SIPS panels; however it is important to address the air tightness of joints between the panels as well as interfaces with other structural elements (i.e. foundation walls or roofs) and penetrations such as windows, doors and services.2 It is relatively easy to achieve a high level of airtightness on a SIPs enclosure.
Typical Insulation: EPS foam is the most common, but SIPs have also been constructed with XPS and polyisocyanurate foam cores.
Durability
Rain Control: Rain leakage into the enclosure is the leading cause of premature building enclosure failure. Rain control is typically addressed using a shingle lapped and/or taped drainage plane such as building paper or a synthetic WRB (i.e. homewrap). Intersections, windows, doors and other penetrations must be drained and/or detailed to prevent the penetration of rainwater beyond the drainage plane.3
Air Leakage Control: There is no air leakage through the centre of the panel but there is risk of air leakage at the joints between panels if not detailed correctly. Historically, there were design detail issues with the air tightness of the joints between the panels allowing warm moist interior air to condense on the exterior cold OSB layer.4 Standards of SIPs construction have improved and following the recommended construction guidelines mitigates nearly all of the risk of moisture related durability issues from air leakage.
Vapor Control: A SIPs panel controls vapor well. There is very minimal risk to vapor related moisture damage in SIPs construction.
Drying: Water on either the interior or exterior of the SIPs will dry easily to the interior or exterior in most climates. In very humid or wet climates with minimal drying potential, the OSB may remain wet for an extended period and could result in moisture related durability issues. Ventilated claddings are recommended and required for this reaason.
Built-in Moisture: Water on the surfaces of the panel during construction should dry easily following completion if ventilated claddings are used; any water trapped in the panel joints will dry much more slowly.
Durability Summary: If the SIPs are installed according to best practice, with proper air seals and flashed penetrations, the system is very durable in all climates.
Buildability
Using SIPs is relatively easy and quick once the training has been completed. Panels are ordered and shipped to site and assembled with a crane. More specific info can be found at www.sips.org. Generally, most of the services are run on interior partition walls, but there are methods of installing services on the interior of a SIPs panel. A SIPs house can be assembled and dried in more quickly than a wood framed house once the panels are on site.
Cost
SIPs panels range considerably in price depending on the project details and the required thickness of wall panels. It is more expensive than standard construction and can generally only be used on simple geometries.
Material Use
SIPs panels require minimal framing lumber but an increase in structural sheathing panels.
Total Score
SIPs wall panels are generally not constructed with enough insulation to be considered a high R enclosure system on its own in heating climates. It is possible to use thicker insulation panels or to combine SIPs with another insulation strategy in cold climates. It is relatively quick and easy to build with SIPs following training, and refined standard practice techniques have removed nearly all of the historical risks of air leakage condensation. The cost and simple geometries of SIPs houses are two of the main reasons why this technology is not used more often.
  2. Lstiburek, J.W. (2008). Builder’s Guide to Structural Insulated Panels (SIPs) for all Climates. Westford: Building Science Press Inc.
  4. SIPA. (n.d.). SIPA Report on the Juneau, Alaska Roof Issue. Retrieved May 2009, from Structural Insulated Panel Association: http://www.sips.org/content/technical/index.cfm?PageId=161
