Search Document Types   →   Enclosures That Work   →   High R-Value Wall Assemblies   →   High R-Value Wall Assembly-03: Interior Strapping Wall Construction
ETW
By Building Science Corporation    Created: 2009/06/05
  • 2x6 advanced framing
  • 2x3 horizontal strapping
  • Fibrous insulation between strapping
  • 6 mil polyethylene air and vapor barrier
  • Fiberglass or cellulose cavity insulation in stud space
  • OSB exterior sheathing
  • Housewrap
Scoring: How It Rates
Thermal Control 3
Durability 3
Buildability 3
Cost 4
Material Use 4
Total
17
Interior strapping in wall construction does increase the R-value over standard construction, but does not address thermal bridges at the rim joist, top plate or bottom plate. The minimal increases in whole wall R-value over standard construction may not be justified by the increased materials, cost and complexity of this wall system.
This Information Sheet summarizes interior strapping wall construction including the advantages and disadvantages of this construction strategy. A more detailed analysis and direct comparison to several other walls can be found online.1 The scoring system is subjective based on the relative performance and specifications between different wall systems. Complex two dimensional heat flow analysis and one dimensional hygrothermal modeling were used to determine moisture related durability risks for analysis.
Installed insulation R-value: There is a range of installed insulation R-values in commercially available fiberglass batts. The installed insulation R-value for 2x6 fiberglass batt ranges between R-19 and R-21 for the framed portion of this wall, and the strapped interior section is typically R-8 fiberglass insulation. When blown or sprayed cellulose insulation is used, the R-value is typically R-20 for 2x6 walls.
Whole-wall R-value: Using two dimensional heat flow analysis with thermal bridging effects and average framing factors, this wall construction achieves a whole wall R-value of approximately R-21.5.1 Adding horizontal strapping to the interior surface helps minimize the thermal bridges through the stud wall, but there are still thermal bridges at the top plate, bottom plate and rim joist that decrease the installed insulation R-value.
Air Leakage Control: Fiberglass batt, and both blown and sprayed cellulose are air permeable materials allowing possible air paths between the interior and exterior as well as convective looping in the insulation. Although densepack cellulose has less air permeance it does not control air leakage.2
Typical insulation: Fiberglass batt, blown fiberglass, blown cellulose, sprayed cellulose.
Durability
Rain Control: Rain leakage into the enclosure is the leading cause of premature building enclosure failure. Rain control is typically addressed using a shingle lapped and/or taped drainage plane such as building paper or a synthetic WRB (i.e. homewrap). Intersections, windows, doors and other penetrations must be drained and/or detailed to prevent the penetration of rainwater beyond the drainage plane.3
Air Leakage Control: Air leakage condensation is the second largest cause of premature building enclosure failure with this type of wall construction. It is very important to control air leakage to minimize air leakage condensation durability issues. An air barrier is required in this wall system to ensure that through-wall air leakage is eliminated (ideally) or at least minimized. An air barrier should be stiff and strong enough to resist wind forces, continuous, durable, and air impermeable.4
Often the polyethylene vapor barrier will be constructed as the air barrier even though it is not stiff or strong enough to resist wind forces. If the polyethylene is installed between the stud wall and the interior strapping, there will be fewer holes made for electrical and plumbing services, and can be made more airtight than in standard construction.
Air need not leak straight through an assembly to cause moisture problems; it can also leak from the inside, through the wall, and back to the inside; or it can leak from the outside, through the wall, and back to the outside. Condensation within the stud space is possible if this type of airflow occurs, depending on the weather conditions. Hence, wall designs should control airflow into the studspace.5
Vapor Control: Fiberglass and cellulose are highly vapor permeable materials, so a separate vapor control strategy must be employed to ensure that vapor diffusion does not result in condensation on, or damaging moisture accumulation in, moisture sensitive materials. The permeance and location of vapor control is dependent on the climate zone. Installing the vapor control layer in the incorrect location can lead to building enclosure failure.6
Drying: Cellulose and fiberglass insulation allow drying to occur relatively easily, so drying is controlled by other more vapor impermeable enclosure components such as the vapor barrier and OSB sheathing. Installing vapor control on both sides will seal any moisture into the stud space, resulting in low drying potential, and possibly resulting in moisture-related durability risks. Ventilation behind vapor impermeable claddings and interior components (e.g. kitchen cabinets) can encourage drying.
Built-in Moisture: Care should always be taken to build with dry materials where possible, and allow drying of wet materials before close in. Cellulose is often sprayed in damp, and manufacturers recommend drying before close in and moisture content limits. If a polyethylene vapor barrier is installed with relatively vapor impermeable OSB sheathing, drying could be slow if built-in moisture is present.
Cellulose insulated walls are slightly more durable because cellulose insulation is capable of storing and redistributing small amounts of moisture. Cellulose insulation is typically treated with borates that have been shown to protect itself and neighboring wood material from mold growth and decay. Cellulose insulation also has decreased flame spread potential relative to other insulation materials.
Buildability
This type of construction is a modification of standard construction, but is not common, and construction trades may have difficulty with some of the detailing. All window and door penetrations will require plywood box frames to pass through both the interior strapping and exterior framing. If the poly is installed properly between the stud wall and interior strapping, there is decreased risk of moisture related durability issues often caused by penetrations such as electrical and plumbing.
Cost
There will be increased costs over standard construction due to an increase in framing material, and complexity for construction, since this is not a standard construction technique. Costs vary tremendously from region to region.
Material Use
Using advanced framing will reduce redundant wood framing in the wall, but overall framing still increases for the interior strapping. Cellulose has a significantly lower embodied energy than fiberglass or rockwool.
Total Score
Interior strapping in wall construction does increase the R-value over standard construction, but does not address thermal bridges at the rim joist, top plate or bottom plate. The minimal increases in whole wall R-value over standard construction may not be justified by the increased materials, cost and complexity of this wall system. Many higher performance designs for wall construction exist.
  2. FINAS. Determination of the air permeability, the short term water absorpition by partial immersion, and the water vapour permeatbility of the blown losse-fill cellulose thermal insulation. Test Report VTT-S-039880-08, VTT Technical Research Centre of Finland, 2008.
  4. Lstiburek, J. (2008, 08 20). BSD-104: Understanding Air Barriers. Retrieved from buildingscience.com.
  5. Straube, J. (2009, 04 22). BSD-014 Air Flow Control in Buildings. Retrieved from buildingscience.com.
  6. Lstiburek, J. (2008, 10 17). BSD-106 Understanding Vapor Barriers. Retrieved from buildingscience.com.