You are here: Home   →   Documents   →   Enclosures That Work   →   High R-Value Enclosure Assemblies   →   High-R Wall-08: Spray Foam Wall Construction
IS
Information Sheets
Created: 2009/06/04
  • 2x6 wood frame wall at 24" o.c.
  • Spray foam cavity insulation
  • OSB sheathing
  • Housewrap
Scoring: How It Rates
Thermal Control5
Durability5
Buildability4
Cost2
Material Use4
Total
20
Both low and high density foam increase the air tightness of the enclosure and reduce the risks to air leakage related durability risks. The R-values of both the low and high density spray foam are significantly reduced by thermal bridging of the wall framing and rim joist, demonstrating the value of insulated sheathing.
This Information Sheet summarizes spray foam wall construction including the advantages and disadvantages of this construction strategy. A more detailed analysis and direct comparison to several other walls can be found online.1 The scoring system is subjective based on the relative performance and specifications between different wall systems. Complex two dimensional heat flow analysis and one dimensional hygrothermal modeling were used to determine moisture related durability risks for analysis.
For a more complete analysis of this and other wall constructions, go to www.buildingscience.com/doctypes/information-sheets.
Installed insulation R-value: The installed insulation R-value depends somewhat on the company and but generally speaking, high density foam (2.0 pcf) ranges between R-5.5-R-6.5 per inch for the aged R-value, and low density foam (0.5pcf) has an R-value of approximately R-3.6/inch. Since high density foam is generally installed short of the cavity to avoid trimming, the installed insulation R-value is approximately R-30 (using R-6/inch). Low density is generally installed deliberately overflowing the cavity and trimmed off resulting in an R-value of approximately R-21.
Whole-wall R-value: Using two dimensional heat flow analysis with thermal bridging effects and average framing factors, it is clear that the thermal bridging through the framing, bottom plate, and top plate reduces the effectiveness of the spray foam insulation.1 The R-value of the high density spray foam wall decreases from an installed R-value of R-30 to approximately R-20, a decrease of R-10 because of thermal bridging. The low density spray foam wall decreases from an installed insulation R-value of 21 to a whole wall R-value of approximately R-16.
Air Leakage – Both low density and high density foam form an air barrier decreasing thermal losses through air leakage. Air leakage is still common under the bottom plate and at the rim joist if these areas are not detailed correctly.2
Typical Insulation: Low density 0.5 pcf foam, or high density 2.0 pcf foam.
Durability
Rain Control: Rain control is typically addressed using a shingle lapped and/or taped drainage plane such as building paper or a synthetic WRB (i.e. homewrap). Intersections, windows, doors and other penetrations must be detailed to prevent the penetration of rain water.3
Air Leakage Control: Air leakage is significantly minimized by installing spray foam insulation in the stud space since both low density and high density spray foam act as an air barrier. This increases the durability of the wall system considerably over standard construction.4
Vapor Control: High density (2.0 pcf) foam forms a vapor control layer reducing vapor movement through the enclosure, minimizing the potential for wintertime vapor condensation and summertime inward vapor drive. Low density foam allows moisture vapor movement through the foam so other methods of vapor control such as poly, kraft paper, or vapor barrier paint may be required based on the geographic location.5
Drying: Both of the spray foam walls dry relatively slowly if water enters the enclosure, since they do not experience convective looping and air movement similar to air permeable insulations. Spray foam does not provide any buffering capacity or redistribution. Foam is relatively moisture tolerant and will be able to dry given enough time. Ventilation behind vapor impermeable claddings and interior components (e.g. kitchen cabinets) can encourage drying.
Built-in Moisture: Care should always be taken to build with dry materials where possible, and allow drying of wet materials before close in. High density foam will inhibit the drying of wet building materials more than low density vapor permeable foam.
Durability Summary: The primary durability risks associated with these wall assemblies involve moisture damage related to rain water penetration. Both air leakage and vapor diffusion durability is significantly increased with spray foam but some vapor control may be necessary with low density spray foam in cold climates.
Buildability
Using spray foam as the stud space insulation is a very simple modification to the construction technique. Generally, the wall construction is the same as standard or advanced framing construction, and spray foam is sprayed into the cavity. Spray foam significantly reduces risks of poor air tightness detailing of the exterior sheathing or interior drywall.
Cost
Using spray foam will increase construction costs considerably but these increased costs may be outweighed by the benefits to energy efficiency, and occupancy comfort from reduced drafts.
Material Use
Wood framing required for spray foam insulation is the same required for the standard construction, or advanced framed wall depending on the framing strategy used.
Total Score
Both low and high density foam increase the air tightness of the enclosure and reduce the risks to air leakage related durability risks. A vapor control (ie. Poly, kraft paper, SVR) with high density foam is generally not required and vapor control with low density spray foam will be climate specific. The R-values of both the low and high density spray foam are significantly reduced by thermal bridging of the wall framing and rim joist, demonstrating the value of insulated sheathing. It may be possible to use spray foam insulation in combination with another insulation strategy to maximize the R-value gained with the spray foam insulation.
  2. Straube, J. (2009, 04 22). BSD-014 Air Flow Control in Buildings. Retrieved from buildingscience.com.
  4. Lstiburek, J. (2008, 08 20). BSD-104: Understanding Air Barriers. Retrieved from buildingscience.com.
